Reminds me of annual tests of feeder cables underground, having to do a continuity test of both conductors and earth, as well as an insulation test of all three phases between and to earth. Long job on a couple of miles of high voltage cable.

As I always stated, the most important conductor is the earth conductor, one can live if we lost a phase, but lose the ground and it's deadly.

Under M&Q Act, if a circuit tripped on earth leakage, we weren't allowed to close the breaker, a test with a megger was required to prove the circuit one way or another. Under NSW, CMR Act, we were allowed to close once and once only, if it held, we considered it was OK, trip again, then a full test of the circuit was required.

 

Over this side of the pond, domestic outlets can be one of two types, quick connect and screw connect. In my opinion, the quick connects should be banned by law. The conductors are held in place by a spring contact, as they age the spring loses tension. I'd hazard a guess 8/10 house fires are caused by those stupid outlets.

 

  • Like 2
Link to post
Share on other sites
  • Replies 13.2k
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Popular Posts

Just got back from QMC again........the last eight days have been a bit Traumatic to say the least,,...blood tests,,X-rays,,and today a visit to a Consultant........cut a long story short......problem

Result........CT Scans all clear......just got letter..been sweating for a fortnight......

Two years ago today..........my life changed forever,,,about this time i was on my way down to the operating theatre for what turned out to be a ten hour operation...........its been life changing in

Posted Images

Bear with me its a long time since I was in the trade over there.

My first question would be what kind of appliance was it behind?  Cooker?  Dryer?  Freezer?

 

Next question would be what size wire gauge is it?   I don't know the metric equivalents of 7.044,  7.029 etc.

 

In my day most cookers didn't have a box behind them.  Just a control on the wall and a short length of 7.044 cable behind them permanently wired in.

In Canada and the US there is a big plug in behind  stoves and dryers so the owner can safely disconnect them.  Wondering if the UK went the same way?

 

Apologies if the above is not helpful.  I'm just curious.

  • Like 1
Link to post
Share on other sites

If it's dead, test and verify, if dead blank it off

If it tests live with no faults you have 3 options 

1 fit a new socket

2 terminate into a connector block and tape it up and cover with a blank plate

3 through crimp each conductor and earth ( live neutral and earth ) and this doesn't need a blank cover and can be plastered over,

All the above conforms to bs 7671.

P.S. make sure to use a voltage tester pen.

 

 

Link to post
Share on other sites
3 minutes ago, mr rob t said:

P.S. make sure to use a voltage tester pen.

 

I'm not a great fan of these, I said earlier they will not prove dead.

You sound like you have some knowledge so reluctantly I say do not give ambiguous instructions to someone clearly not trained.

You have not proved dead, you cannot say to an untrained person 'test and verify'. You have no idea if the cable is damaged somewhere so will your test include an insulation test, continuity test or a polarity check? You have no idea of the instruments or tools he has available. Quoting the regs tells him nothing...

 

Link to post
Share on other sites
2 hours ago, loppylugs said:

Bear with me its a long time since I was in the trade over there.

My first question would be what kind of appliance was it behind?  Cooker?  Dryer?  Freezer?

 

 My understanding is no one knows loppy. It may be a circuit that was never completed and doesn't connect in the consumer unit or it may be some clown disconnected an appliance and just left it. 

To me giving advice to someone you don't know about something you haven't seen and has the potential to kill is foolish in the extreme.

Standing in a coroners court and saying 'that's not what I meant' is not a lot of good.

 

To answer your question mate:-

 

Imperial Cable Size Metric Cable Equivalent
1/.044 1.0 mm²
3/.029 1.5 mm²
3/.036 ?
7/.029 2.5 mm²
7/.036 4.0 mm²
7/.044 6.0 mm²
7/.052 10.0 mm²
7/.064 16.0 mm²
19/.044 ?
19/.052 25.0 mm²
19/.064 35.0 mm²

 

For lighting and mains the majority of wiring is in twin and earth solid core, 6mm and above is usually multi- strand T&E (I can't remember if 4mm is multi or not, havn't specced it in years)

  • Like 1
Link to post
Share on other sites

Well in the end it was a bit of a non event.

 

The 'socket' is behind a narrow wine refrigerator fitted between cupboards.  Daughter was intending to take wine fridge when moving as purchaser wasn't interested in paying a fair price for it.

 

So.. when I got there bearing a  used, but functioning and good quality ( MK ) socket, tape, terminal blocks etc.. and tools.. it became obvious that there was insufficient space for me to get both hands into the space to work on anything.  I did manage to get a neon type tester in, but there was no visible bare conductor on live or neutral and I could get no 'reading'.  The earth was accessible but sleeved and showed no reading. The socket was formerly used to supply a dishwasher.  Immediately above was a fused switch unit with four switches.  All checked out as supplying their labelled appliances, including one which supplies a dishwasher in a new position.

I strongly suspect that the short wiring 'drop' to the open socket has been removed/disconnected from the fused switched outlet.

 

Also, it was obvious that removing the wine fridge could only be accomplished by removing its moulded mains plug, which was left no way out from where it was situated.. plugged into yet another socket, fitted inside a cupboard.

 

So.. the conclusion was.. put everything back and leave 'as is'.  I.E. as left by kitchen fitters.  Since I had the misfortune to use the same kitchen fitter, I know him to have the mechanical aptitude of a slug. It will be he who fitted the wine fridge and trapped the plug.   His plumbing skills are abysmal and I could do far better, even though I'm not a plumber.  However, the electrics were done by the same chap who did the electrics in my kitchen and I'm confident that his work is up to standard and safe.. so, we work on the assumption that if he left it like that.. it is safe.  If anyone else decides to take out the wine fridge and start playing with wires.. that is their problem and they are only playing with what was left by the fitters.

 

  • Like 1
Link to post
Share on other sites

Sounds like you got it sorted, Col.  good  Probably best let sleeping dogs lie and all that.

 

Thanks for the info, Brew.  Metric was just coming in when I left the UK 70/71.

I had to quickly get used to American Wire Gauge,  AWG.

# 14  Good to 15 amps used for most lighting and recepticles

# 12 Up to 20 amps .  Mostly separate circuits for dishwashers

 

Code allows only up to 80% loading on any circuit

# 10       30 amps  Clothes dryers mostly

# 8          40 amps stoves / cookers

 

The above is for copper conductors.  You had to go up a size for equivalent aluminum.  Not used much in branch circuits anymore.  Too many problems.

 

We often used # 3 .   Three seperate conductors in conduit for 100 amp services.  These were all 120/240 volt three wire.  120 for lighting and plugs.  240 for stoves dryers.  Funny things happened if the neutral ever failed.   I've never really liked it.  Prefer the UK straight two wire 240v.

So now you have enough info to wire a Canadian house.  US code has a few different rules but is very similar.

Link to post
Share on other sites

What always worries me is US style mains plugs.  Two thin wobbly pins and no earth. . similarly poor plugs in continental Europe too... but with round rather than flat pins  Although it can be a PITA, it seems to me that the UK style is very well thought through.

A 'gate' opened first by the earth pin, before the live and neutral can even enter the socket.. and a fuse as an integral part of the plug.

 

There was a bit of an issue years ago.. when the EU decided that 4mm 'banana' pugs as used for loudspeaker connections.. needed to be banned, because some clown had plugged a passive speaker into the mains and was surprised when it blew up.  This because the EU mains pins are also 4mm.  After a while.. it all seemed to go away.. and I have to say that it is no reason to support Brexit!! ;)

 

  • Like 1
Link to post
Share on other sites
1 hour ago, DJ360 said:

Well in the end it was a bit of a non event.

 

 

Alls well that ends well...

 

20 minutes ago, loppylugs said:

So now you have enough info to wire a Canadian house.  US code has a few different rules but is very similar.

 

My days of crawling round pulling cable are long gone,  Loppy         long gone

  • Like 1
Link to post
Share on other sites

I know what you mean, Col.  I didn't like them when I first got here.  They can get surprisingly warm when you plug in a heavy load like a kettle or heater.  In general use though they seem quite durable and I only had to replace very few in 25 years in the trade in Canada.

I liked the British 13 amp sockets.  They always seemed well built.  Main strike against them for me was that they are not fool proof and the 13 amp fuse  tended to be left in for light loads like table lamps, radios etc.  Thus defeating the object.  All electrical items here tend to come with the plug already moulded on.  You can buy beefier ones from the hardware store if you really want to.

  • Like 1
Link to post
Share on other sites
13 minutes ago, Brew said:

 

 

My days of crawling round pulling cable are long gone,  Loppy         long gone

 

Same here, Brew.  The thought of time in an attic when its 95 outside would do me in.  I'm definitely not going in crawl spaces in Georgia.  You could meet a snake.  My wire pulling days are over.

Link to post
Share on other sites
18 minutes ago, loppylugs said:

I know what you mean, Col.  I didn't like them when I first got here.  They can get surprisingly warm when you plug in a heavy load like a kettle or heater.  In general use though they seem quite durable and I only had to replace very few in 25 years in the trade in Canada.

I liked the British 13 amp sockets.  They always seemed well built.  Main strike against them for me was that they are not fool proof and the 13 amp fuse  tended to be left in for light loads like table lamps, radios etc.  Thus defeating the object.  All electrical items here tend to come with the plug already moulded on.  You can buy beefier ones from the hardware store if you really want to.

 

Fair point Dave,

I do try to put in appropriate fuses rather than just having the Brown 13A in all plugs.

 

For my Hi-Fi stuff, I use good quality MK sockets and MK or Crabtree plugs. I also keep the pins very clean.  I have no idea if this makes any real improvement.. but it does no harm.

  • Like 1
Link to post
Share on other sites

There is a question in the PAT (Portable Appliance Test) exam about the size of fuses to fit to plugs. The answer is either 5 or 13 amp depending on the size of the cable.  Fuses protect cables not appliances as I was forever telling apprentices.

 

There seems to be variations on NEMA plugs, and  similar differences with  the European SHUKO, at least we have one size fits all.

There was a move some years ago to unify the design for Europe, but it had to be a design that was totally original  - never got of the ground.

  • Like 1
Link to post
Share on other sites

I live only a few kilometres from Nice and I can tell you that it most certainly won't boast 300 days of sunshine this year. I've lived here for over 30 years and this is, by far, the worst weather I've ever known. NonnaB (who lives not too far away) is having even worse weather than here.

 

I live quite high in the mountains so it's unlikely I will get seriously flooded (heaven help the coastal conurbations if I do!) but I can tell you that there is an awful lot of water flowing in the rivers.

Where I live (I posted this a few weeks ago):

Quote

The only low level place I've lived is the flat I had next door to the Grosvenor on Mansfield Road. I was there at the time of the 'big storm' in about 1972 see https://nottstalgia.com/forums/topic/17313-the-grosvenor-pub/?tab=comments#comment-591022

 

 

Otherwise my home has been quite elevated and, at present, I live a good way up a mountain gorge (on the first picture of the link, my villa is just visible towards the top, right.

http://freeriders2.over-blog.com/article-30273517.html ) Note: the link is to a French bikers blog and it's in French but don't let that put you off. It offers a good illustration of life in le BsL.

 

The weather is not too bad today. Certainly warmer than it has been over the last week but not a lot of sun showing through.

Link to post
Share on other sites

12" to 18" of snow forecast this week in parts of the mid west, that's a lot of snow from one snow storm!!

Link to post
Share on other sites

Thankfully it won't be us, too far south for snow that heavy, but there will be many people it affects, think of all the truckers trying to earn a crust and trying to get home for our Thanksgiving holiday to see their families, stuck at a truck stop for a few days.

 

Link to post
Share on other sites

Dave, that takes me back to when I rewired the house we bought in Australia, stripped to my shorts in the roof space running cables out, 100 plus outside, tin roof too!!

Mind, I worked at Boulby for nearly five years, when I worked in a district the coolest spot was 90F and that was our snap cabin, try 110 plus in the faces!! Mind the only cables I pulled down there were heavy trailing cables that few the machines.

I planned my days on this house when I built it, ran all the cables out prior to gyprocking the ceilings.

  • Like 1
Link to post
Share on other sites
1 hour ago, Beekay said:

Some beautiful pictures of your gaff Jonab. Looks a picturesque  area and oooh, all those lovely oranges.

 

Those oranges in the basket on the chair with the note "Servez vous" (Help yourself) are placed deliberately for unsuspecting tourists that come to the orange festival held each Eastertide. The oranges are bigarades - bitter oranges (similar to Seville oranges) and are completely inedible as a fresh fruit. The oranges are used in the perfumery industry (leBsL is very close to Grasse), for making the local orange wine, preserves (like marmalade) and the peel (which you see hanging up in one of the pictures) is dried and used for making orange liqueurs like Triple Sec, Grand Marnier and Cointreau and numerous others.

  • Like 1
Link to post
Share on other sites

Sunny...sort of today. It's keeps peeping out to have a look and then hides behind the nearest cloud. Yes we eventually had water coming through the house but it wasn't too bad, it mopped up easily but it's made us realize that at the back of the house more work has to be done. Years ago we had a courtyard at the back of the hose and we had an extra room built along with a couple of store rooms. It was ok for a few years until we had "the rainy season" . We didn't know until a neighbour told us that the builder that did the work didn't put in drainage as the land slopes down towards the house. We called him back and the answer was " you didn't tell me to" Whose the builder here? Anyway the wall was knocked down and it's been ok but this seems now to be coming through from either next doors cantina or upwards through the tiles. The house is about 150- 200 yrs old so probably hasn't got today's standard of foundations. But it's still standing.

  • Like 1
Link to post
Share on other sites

Busy week..starting today.

 

Both daughters are moving house..  so I'm on Curtain Rail duty.. along with sundry other tasks,. We also have  No.1 daughter's cat while she moves.

 

 Young 'un ..moved into her first house with her partner yesterday. A couple of miles closer to us at around 18 miles. We went around today and I was happy to stand back while her boyfriend showed hitherto hidden skill in fitting a curtain rail.  Obviously I had to provide tools and copious advice.. but his Dad is a builder back in St Vincent, so he's clearly picked up a few skills. His Army training did him no harm either and he's a very quiet.. calm lad.. in sharp contrast to No.2 Daughter.. 

Daughter had a bit of a meltdown as she left her previous accomodation... a fabulous Art Deco 1930s house which she loved.. and shared with three or four others who she got on with very well.  New place is a new build rental in a rather less 'posh' area.. but seems OK. 

It's a concern just how precarious many young people's lives are these days.  No.1 daughter is a very talented designer with 10 years experience in fashion.. but her jobs are rarely very secure and she has redundancy over her head again so is prepping for interviews at same time as moving.  Her boyfriend earns good money.. but works long and anti social hours for it. again with little job security.  Still.. both have supportive families, good education etc..  Many are far, far worse off.. and on reflection.. we had it pretty rough and uncertain through the 70s,80s and 90s. but we hung in there..

 

Oldest and Son in Law are moving to a bigger.. better place in a new development.. with the Grandkids obviously...

He does something to do with Credit Card Fraud...  I mean... not so much doing it.. as stopping it..  :)

She is  a HR Manager, but she's seriously visually impaired so has to use public transport for work.  I have to keep telling her to use her white stick.. because she's reluctant to do so.

Grandkids will go to school from their old house on Friday.. but will go home to their new house.  I'm picking them up from school.  I may bring them to our house overnight to give their Mum and Dad a break, before delivering them to their new home on Saturday.  That'll be interesting.  Will they be more excited by a sleepover at ours.. or their first sleep in their new house?  Oh! how simple were the joys of youth... 

 

I sometimes think I'd like to have another go at life.. starting all over again...  But then I think.. really?  Could you put up with all that again?

 

Leave it to the youngsters.. if there's anything left to leave...

 

I'm not half as morose as it sounds... :laugh:  Just a bit reflective.

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...